I’m not sure how many of you play with this sort of stuff but I’m on my own in this one and hope someone might have an idea. Currently 10.30pm on nightshift, I’m commissioning a crushing plant and I can’t get a belt (from primary crusher to screen house) to go.
It has two x 75kW motors, I have isolated individually and bumped to determine correct direction but it’s very hard to tell as it barely moves. They are both DOL and turning the instant trip right up to a bit over 1250 amps each is the only way to stop each one tripping its breaker, but something won’t let it turn as it trips out on overload a few seconds later.
With fan cover off I can turn it a smidge by hand to confirm direction which suggests there is NOT an issue with an incorrect backstop in one of the gearboxes.
I have the crushers off and two x 1 MW generators are on to feed the show so power shouldn’t be an issue in any way.
This is from the tail end.
So any ideas? I don’t think the backstops are an issue (but I’m not positive), motors are clearly quite loaded until they trip and I don’t want to destroy the sprag clutches or I’ll never hear the end of it from the mechs.
@Overboard @Haggie
Any thoughts if anyone plays with this stuff would be great. Meanwhile I have to calibrate the rock breaker so I’ll get back to this later.